Hey Alex,

> [@Dr-Al](#):
>
> Then an EMI filter would be better.

the EMI filter on the input side of a VFD is to protect the house installation and other electrical devices connected to it from the EMI the VFD produces.

> ![Omron_MX2_Manual __General_Warnings_and_Cautions__ PXVII__Suppression_for_Noise_Interference_from_Inverter](https://us1.discourse-cdn.com/flex022/uploads/onefinitycnc/original/2X/0/095a61734100d077538d755c5cd87f92fd2e9492.png)  
> – Source: [Omron MX2 User’s Manual](https://assets.omron.eu/downloads/manual/en/v5/i570_mx2_users_manual_en.pdf)

What protects the VFD from power distribution system is the input-side AC reactor:  
 ![Omron_MX2_Manual __General_Warnings_and_Cautions__ PXVII__Effects_of_Power_Distribution_System_on_Inverter](https://us1.discourse-cdn.com/flex022/uploads/onefinitycnc/original/3X/3/5/35daeaa00f192cb5f0dc7926c86c5e12f345d4a9.png)

 ![Omron_MX2 __Basic_System_Description__ P028_pdf054](https://us1.discourse-cdn.com/flex022/uploads/onefinitycnc/original/3X/7/6/76f4dd5ee355b59ac300d7c934794d4fd9a63137.png)

---