Hey Owen,

thanks for the photo of VFD nameplate.

What it says is:

- The VFD can deliver 180-250 V 3-phase current with 15 A at its output,  
but
- the rated 10 A at its input is obviously the value for 3-phase input, which means, _per phase_. You have a VFD model that you can attach on single-phase or on three-phase electricity. Unfortunately the rated input current for operation on single-phase electricty is not mentioned on your nameplate.

But if you look at my nameplate on a VFD with the same parameters (by coincidence) I know that if you use it on single-phase supply, the maximum input current would be about at least 20 A.

By coincidence the values of your spindle and your VFD both correspond to mine, except that my VFD is offered for one phase input and for three-phase input as separate models. Since in Europe we usually have either three-phase electricity with 400 V or single-phase with 230 V, the _200 V three-phase_ model is of no use (it suits U.S. 208 V industrial three-phase electricity), so you have to use your VFD with 230 V single-phase if you’re in Europe.

What unfortunately is not mentioned on your nameplate, is the max current if you use it with one phase input. On my VFD, which is also a 200 V class, 2.2 kW VFD with single phase input, it is rated with 20 A max. input current in CT mode and 24 A in VT mode.

You can see in this table that the 200 V class 2.2 kW (CT mode) version on _single-phase input_ requires a 30 A fuse (a one-phase [MCCB](https://en.wikipedia.org/wiki/Circuit_breaker#Low-voltage)), but the same model with 200 V class _three-phase input_, you need only 15 A fuse, _but that is one fuse per phase(!)_, which means that would be a **3** x 15 A MCCB. This way you can judge on what the 10 A input on your VFD means, it means, _per phase_, if you would have three-phase input. But on one phase, it is logical that it would have more rated ampères since all the power would come from one single wire, thus the need for larger current, larger fuse and thicker wires then. Wire and fuse size do not depend on input power (kVA), but on current (in ampères)

> [@What is needed to wire up 2.2kw 220v Spindle and VFD?](https://forum.onefinitycnc.com/t/what-is-needed-to-wire-up-2-2kw-220v-spindle-and-vfd/11123/22):
>
> > [@What is needed to wire up 2.2kw 220v Spindle and VFD?](https://forum.onefinitycnc.com/t/what-is-needed-to-wire-up-2-2kw-220v-spindle-and-vfd/11123/2):
> >
> > In my VFD manual, it says:
> > 
> > > ![Omron_MX2 __2-3-6__ Determining_Wire_and_Fuse_Sizes_P045_pdf071__cropped_v2](https://us1.discourse-cdn.com/flex022/uploads/onefinitycnc/original/2X/a/a3e0d9a359d77637444cbf6d8dc96b282fc2a6c9.png)
> > > 
> > > – Source: [Omron MX2 User’s Manual](https://assets.omron.eu/downloads/manual/en/v5/i570_mx2_users_manual_en.pdf)

That means that at its input, I have **2+PE × 4 mm²** cable and at the output for the 2.2 kW / 8 A three-phase spindle, I have **3+PE × 2.5 mm² _shielded_** wire.

For the VFD with 20 A input on one phase, this means the usual 16 A household circuit is not enough, so I have a [Blue P+N+E 6h/32 A CEE](https://en.wikipedia.org/wiki/IEC_60309#Blue_P+N+E,_6h) wall outlet (see image in posting below) on a 32 A one-phase MCCB.

> [@OwenH](#):
>
> I am in Europe so 220v is standard and single phase. Here is a picture of the plate on the VFD. If you think I am better buying a new VFD can you recommend one that will not break the bank.

I think it’s very okay to buy the cheap spindles and VFDs if you are new and want to get in contact with the matter. The reason why I don’t always mention what I bought is that it _will_ break the bank for many hobbyists, but I plan to use the equipment professionally. What I bought is decribed here:

> [@Spindles - Lingering Questions](https://forum.onefinitycnc.com/t/spindles-lingering-questions/8643/24):
>
> I bought the [Mechatron HFS-8022-24-ER20](https://www.spindel-shop.de/en/High-Frequency-Spindle-standard-Series/High-Frequency-Spindle-HFS-series/Water-Cooled-HF-Spindles--HF-Spindle--HF-Spindles--HF-Spindle--HF-Spindles--Motorspindle--Milling-Spindle--Grinding-Spindle-4.html) ([Specifications](https://www.mechatron-gmbh.de/fileadmin/user_upload/Datenblatt_HFS-8022-24-ER20.pdf)) earlier this year for 899,00 € (approx. $1058.35¹) but now the price is 970,92 € (approx $1120.98¹),
> 
> the [Mechatron Cooling Station KG5000](https://www.spindel-shop.de/en/Cooling/Cooling-Systems/Kuehlgeraet-KG5000.html) I bought earlier this year for 771,12 € (approx. $907.80¹) but now the price is 832,81 € (approx. $961.52¹)
> 
> the [Omron 3G3MX2-AB022-E](https://industrial.omron.co.uk/en/products/mx2) bought earlier this year for 357,00 € (approx. $420.28¹), but this one did not change its price, but it’s not available now at the moment in the shop where we bought it.
> 
> Also the [Phoenix M17 Connector](https://www.phoenixcontact.com/en-us/products/circular-connector-cable-side-st-3es1n8a8005-1624537) for the spindle changed from 29,04 € to 31,90 €.
> 
> Many things have become more expensive during the last two years and many are not available, I assume on the one hand because for the suppliers the costs for international transport have exploded (up to 1200%) and on the other hand because many goods are difficult to obtain, e.g. computer chips. So I’m lucky that I bought my stuff already.
> 
> * * *
> 
> 1.) As of 2021-11-04, Euro exchange rate may be different today

Note that I would not buy the Omron MX2 in its single-phase version again, but always prefer the version for 400 V three-phase input. But at the time I bought my stuff the three-phase 400 V model was not available. We have 400 V three-phase in every house here (in the circuit breaker box). This would have allowed me to use thinner cable at the input (3+PE with 2.5 mm² wire size instead of 2+PE x 4.0 mm², and a 3 x 16 A MCCB instead of a 1 x 32 A MCCB).

Note that the [Omron MX2](https://industrial.omron.co.uk/en/products/mx2) is practically identical to the [Hitachi WJ200](https://www.hitachi-ies.co.jp/english/products/inv/wj200/index.htm), also the manuals are nearly identical ([Manual](https://assets.omron.eu/downloads/manual/en/v5/i570_mx2_users_manual_en.pdf) / [Manual](https://www.hitachi-iesa.com/sites/default/files/supportdocs/WJ200_Instruction_NT325X.pdf)). The 200 V class **one-phase input** 2.2 kW model that corresponds to [Omron 3G3MX2-AB022-E](https://industrial.omron.co.uk/en/products/mx2) is Hitachi WJ200-022SF.

By the way the same spindle I bought is already in use by two forum members here and the Hitachi WJ200 also by two people.

PS: Will fill in WWW links later!

---