Hey Rob,
Cables
for connecting your new cables to the machine here are the
- Specifications for the Cable Connectors Used on the Onefinity.
For doubt about these Molex/Amphenol connectors and better replacing them everywhere (while you’re at it), please see here.
For choosing cables:
- If you have a spindle, see please see this.
- For the trim router and the stepper cables, here.
If you want water cooling hoses later too, I suggest a profile of at least 15x40.
Emergency Stop
An Emergency Stop for a spindle is NEVER between spindle and VFD. This is written in the first pages of every VFD manual, even in the cheap Huanyang VFD manual!
An Emergency Stop for a spindle would not power off the VFD either, but activate one of the Intelligent Terminals on the VFD which you would have programmed to serve as ISO 13849-1 Safety Inputs, or similarly programmed to initiate the spindle stop command. You can wire an Emergency stop switch directly to the VFD, or make use of a ISO 13849 Safety relay such as a Omron G9SE (datasheet), wired as follows:
(Source: Omron MX2 User’s Manual)
(Source: Hitachi WJ200 Instruction Manual )