VFD is flashing "200.00"

Hey David,

if it says “Timed out”, then there is no connection. I would check/replace the cable. I think the problem can be solved this way easily and you will not despair anymore :slight_smile:

You are right, there is no wire gauge and wire ferrule specification in the S1 Manual, but there is this hit for “AWG”:


By accident, I had looked into the Hitachi WJ-C1 manual instead.

However, there is a specification for the wire gauge for signal cables and the wire ferrules in the WJ-C1 manual on the page 5-4-7:


Here you see the wire gauges and the wire ferrules specifications.


This is how to insert them into the VFD terminals (on WJ-C1, sorry!).

The RS-485 serial connection is a balanced connection and using a shielded, twisted pair communications cable is recommended.