Redline VFD Spindle Error Codes (FAQ)

Errors Codes on the Onefinity Spindle Kit by Redline CNC VFD Display used for troubleshooting


Error 1:

Description: Over-current at constant speed - The output current exceeds the over-current value while the frequency inverter is running at a constant speed

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s low
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 2:

Description: Over-current at acceleration - When the frequency inverter accelerates, output current exceeds over-current

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s low
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 3:

Description: Over-current at deceleration - When the frequency inverter decelerates, output current exceeds over-current

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s low
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 4:

Description: Over-voltage at constant speed - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. Detected DC over-voltage value: Level T2 : 400V

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s high
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 5:

Description: Over-voltage at acceleration - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. The detected over-voltage value is the same as above.

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s high
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 6:

Description: Over-voltage at deceleration - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. The detected over-voltage value is the same as above.

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s high
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 7:

Description: Module fault - External fault has triggered automatic module protection

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 8:

Description: Under-voltage - Under-voltage in the main circuit, check the electric level: Detected DC under-voltage value: Level T2 : 190V

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 9:

Description: Frequency inverter overloaded - Motor and current exceed the rated load

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 10:

Description: Motor overload - Motor and current exceed the rated current

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 11:

Description: Missing phase - Error of missing phase or unbalanced three phases

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check wall circuit voltage for missing phase or unbalanced three phases
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 12:

Description: Output Default Failure - Output Default Failure or 3-phase Imbalance Fault

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 13:

Description: External Fault - Fault caused by External Control Circuits

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 14:

Description: Abnormal Communication - Abnormity for communication of frequency inverter and other equipment

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 15:

Description: Frequency inverter Overheat - Radiator temperature ≥ oh Detection Value (about 80℃, from temperature switch)

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check to ensure spindle motor fan is running
  • Check whether the surrounding temperature is too high and cooling measures are required
  • Clear dirt, dust, debris from the air intake on the top of the spindle motor
  • Contact technical support

Error 16:

Description: Hardware Fault of Frequency inverter - In case of over-current or over-voltage existed in frequency inverter, it is judged as hardware fault

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Check your wall outlet voltage to see if it’s low or high
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 17:

Description: Motor-to-ground short circuit - Motor-to-ground short circuit

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 18:

Description: Motor Identification Error - When conducting the parameter identification, the fault occurs in motor

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 19:

Description: Motor Off-load - Refer to the value of running current less than off-load current P6.1.19 and duration of P6.1.20

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 20:

Description: PID Feedback Loss Refer to the value of PID feedback value less than value of P4.0.18 and duration of P4.0.19

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 21:

Description: User-Defined Fault 1 - Fault 1 Signal given by the users through multi-functional terminals or PLC Programming Function

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 22:

Description: User-Defined Fault 2 - Fault 2 Signal given by the users through multi-functional terminals or PLC Programming Function

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 23:

Description: Accumulative Power-on Time Arrival - Refer to the time given by accumulative power-on time arrival P5.1.01 of the frequency inverter

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 24:

Description: Accumulative Running Time Arrival - Refer to the time given by accumulative power-on time arrival P5.1.00 of the frequency inverter

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 25:

Description: Encoder Fault - The frequency inverter is unable to identify the data of the encoder

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 26:

Description: Parameter Read-Write Abnormity - Damage of EEPROM Chip

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 27:

Description: Motor Overheat - Detection on excessive temperature of the motor

Troubleshooting:

  • Check whether the temperature of the motor is too high
  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 28:

Description: Larger Speed Deviation - Refer to the value of speed deviation larger than P6.1.23 and duration of P6.1.24

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 29:

Description: Motor Over-speed Refer to the value of motor speed over P6.1.21 and duration of P6.1.22

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 30:

Description: Initial Position Error - Large deviation between motor parameters and actual parameters

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 31:

Description: Current Detection Fault - Circuit fault after current detection

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 32:

Description: Contactor Abnormal power supply of driver board caused by the fault of the contactor

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 33:

Description: Abnormity of Current Detection - Circuit fault after current detection leads to abnormal current detection value

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 34:

Description: Fast Current-limiting Timeout - The running current of the frequency inverter continues to be larger, which exceeds allowable current–limit time

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 35:

Description: Motor Switch at Running - Conduct motor switch in the running process of the frequency inverter

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support

Error 36:

Description: Power Fault - External 24V power supply is short circuit or the load of External 24V power supply is too large

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Contact technical support

Error 40:

Description: Buffer Resistance - The bus voltage fluctuates strongly

Troubleshooting:

  • Check cables to ensure they are properly connected
  • Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
  • Contact technical support