Errors Codes on the Onefinity Spindle Kit by Redline CNC VFD Display used for troubleshooting
Error 1:
Description: Over-current at constant speed - The output current exceeds the over-current value while the frequency inverter is running at a constant speed
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s low
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 2:
Description: Over-current at acceleration - When the frequency inverter accelerates, output current exceeds over-current
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s low
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 3:
Description: Over-current at deceleration - When the frequency inverter decelerates, output current exceeds over-current
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s low
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 4:
Description: Over-voltage at constant speed - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. Detected DC over-voltage value: Level T2 : 400V
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s high
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 5:
Description: Over-voltage at acceleration - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. The detected over-voltage value is the same as above.
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s high
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 6:
Description: Over-voltage at deceleration - When the frequency inverter runs at constant speed, DC voltage of the main circuit exceeds this set value. The detected over-voltage value is the same as above.
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s high
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 7:
Description: Module fault - External fault has triggered automatic module protection
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 8:
Description: Under-voltage - Under-voltage in the main circuit, check the electric level: Detected DC under-voltage value: Level T2 : 190V
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 9:
Description: Frequency inverter overloaded - Motor and current exceed the rated load
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 10:
Description: Motor overload - Motor and current exceed the rated current
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 11:
Description: Missing phase - Error of missing phase or unbalanced three phases
Troubleshooting:
- Check cables to ensure they are properly connected
- Check wall circuit voltage for missing phase or unbalanced three phases
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 12:
Description: Output Default Failure - Output Default Failure or 3-phase Imbalance Fault
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 13:
Description: External Fault - Fault caused by External Control Circuits
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 14:
Description: Abnormal Communication - Abnormity for communication of frequency inverter and other equipment
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 15:
Description: Frequency inverter Overheat - Radiator temperature ≥ oh Detection Value (about 80℃, from temperature switch)
Troubleshooting:
- Check cables to ensure they are properly connected
- Check to ensure spindle motor fan is running
- Check whether the surrounding temperature is too high and cooling measures are required
- Clear dirt, dust, debris from the air intake on the top of the spindle motor
- Contact technical support
Error 16:
Description: Hardware Fault of Frequency inverter - In case of over-current or over-voltage existed in frequency inverter, it is judged as hardware fault
Troubleshooting:
- Check cables to ensure they are properly connected
- Check your wall outlet voltage to see if it’s low or high
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 17:
Description: Motor-to-ground short circuit - Motor-to-ground short circuit
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 18:
Description: Motor Identification Error - When conducting the parameter identification, the fault occurs in motor
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 19:
Description: Motor Off-load - Refer to the value of running current less than off-load current P6.1.19 and duration of P6.1.20
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 20:
Description: PID Feedback Loss Refer to the value of PID feedback value less than value of P4.0.18 and duration of P4.0.19
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 21:
Description: User-Defined Fault 1 - Fault 1 Signal given by the users through multi-functional terminals or PLC Programming Function
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 22:
Description: User-Defined Fault 2 - Fault 2 Signal given by the users through multi-functional terminals or PLC Programming Function
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 23:
Description: Accumulative Power-on Time Arrival - Refer to the time given by accumulative power-on time arrival P5.1.01 of the frequency inverter
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 24:
Description: Accumulative Running Time Arrival - Refer to the time given by accumulative power-on time arrival P5.1.00 of the frequency inverter
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 25:
Description: Encoder Fault - The frequency inverter is unable to identify the data of the encoder
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 26:
Description: Parameter Read-Write Abnormity - Damage of EEPROM Chip
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 27:
Description: Motor Overheat - Detection on excessive temperature of the motor
Troubleshooting:
- Check whether the temperature of the motor is too high
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 28:
Description: Larger Speed Deviation - Refer to the value of speed deviation larger than P6.1.23 and duration of P6.1.24
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 29:
Description: Motor Over-speed Refer to the value of motor speed over P6.1.21 and duration of P6.1.22
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 30:
Description: Initial Position Error - Large deviation between motor parameters and actual parameters
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 31:
Description: Current Detection Fault - Circuit fault after current detection
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 32:
Description: Contactor Abnormal power supply of driver board caused by the fault of the contactor
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 33:
Description: Abnormity of Current Detection - Circuit fault after current detection leads to abnormal current detection value
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 34:
Description: Fast Current-limiting Timeout - The running current of the frequency inverter continues to be larger, which exceeds allowable current–limit time
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 35:
Description: Motor Switch at Running - Conduct motor switch in the running process of the frequency inverter
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support
Error 36:
Description: Power Fault - External 24V power supply is short circuit or the load of External 24V power supply is too large
Troubleshooting:
- Check cables to ensure they are properly connected
- Contact technical support
Error 40:
Description: Buffer Resistance - The bus voltage fluctuates strongly
Troubleshooting:
- Check cables to ensure they are properly connected
- Conduct VFD Programming Factory Reset and manually input programming codes found in Redline CNC Spindle Kit User Manual
- Contact technical support