PS: The other day you said:
The nameplate rating of the VFD would only be used if the manual does not contain specific information
Here both say the same, manual and VFD.
If you want to say, if the input rating is missing, you can do nothing, and you refuse to connect this VFD, then I support that. Better than connecting it to an underdimensionated circuit. But I think you can very well calculate the approx. input rating based on the knowledge about single and three-phase electricity and how a VFD works. And I strongly believe that for a VFD sold for the 2.2 kW spindles they also offer, I am very sure that by dimensionatig a 45 A circuit, you are on the very safe side.