Recommended Huanyang Configuration
Unlock VFD Config
PD000 SET 0 SET – UNLOCK VFD CONFIG
Initial Configuration provided HY for my 110V 2.2kw water spindle (Check your own manual)
PD005 SET 400 SET – DEFINE MAX FREQUENCY SETTING TO: 400.00 Hz (default was 50.00)
PD004 SET 400 SET – DEFINE BASE FREQUENCY SETTING TO: 400.00 Hz (default was 50.00)
PD002 SET 1 SET – DEFINE SOURCE OF OPERATING FREQUENCY SETTING TO: SET BY EXTERNAL TERMINALS. (default was 0)
PD070 SET 1 SET – DEFINE ANALOG INPUT SETTING TO: 0~5V (default was 0)
PD072 SET 400 SET – DEFINE HIGHER ANALOG FREQUENCY SETTING TO: 400 (default was 50.00)
PD144 SET 3600 SET – DEFINE RATED MOTOR REVOLUTION SETTING @60Hz TO: 3600 (default was 1440) or 3000 for 50Hz
PD008 SET 110 SET – DEFINE MAX VOLTAGE SETTING TO: 110V (default was 220)
Configuration for automatic control with 1F communication
PD001 SET 2 SET – DEFINE SOURCE OF OPERATING COMMANDS SETTING TO: SET BY COMMUNICATIONS PORTS AS COMMAND SOURCE (default was 0)
PD002 SET 2 SET – DEFINE SOURCE OF OPERATING FREQUENCY SETTING TO: SET BY COMMUNICATION PORTS. (default was 0)
PD163 SET 1 SET – DEFINE COMMUNICATION ADRESSES SETTTING TO: 1 - MUST MATCH ONEFINITY BUS-ID (default was 0)
PD164 SET 1 SET – DEFINE COMMUNICATION BAUD RATE SETTING TO: 9600 – MUST MATCH ONEIFINITY BAUD (default was 1)
PD165 SET 3 SET – DEFINE COMMUNICATION DATA METHOD SETTING TO: 8N1 for RTU – MUST MATCH ONEFINITY PARITY
Configuration to trigger SSR (i.e start pump and vacuum)
PD052 SET 2 SET – DEFINE Multi-Output 3(FA, FB, FC function)
PD053 SET 1 SET – DEFINE Multi-Output 4 (KA, KB function)
Lock VFD Config
PD000 SET 1 SET – Lock config