Information to build you own Onefinity Companion Control Box

Recommended Huanyang Configuration

Unlock VFD Config

PD000 SET 0 SET – UNLOCK VFD CONFIG

Initial Configuration provided HY for my 110V 2.2kw water spindle (Check your own manual)

PD005 SET 400 SET – DEFINE MAX FREQUENCY SETTING TO: 400.00 Hz (default was 50.00)

PD004 SET 400 SET – DEFINE BASE FREQUENCY SETTING TO: 400.00 Hz (default was 50.00)

PD002 SET 1 SET – DEFINE SOURCE OF OPERATING FREQUENCY SETTING TO: SET BY EXTERNAL TERMINALS. (default was 0)

PD070 SET 1 SET – DEFINE ANALOG INPUT SETTING TO: 0~5V (default was 0)

PD072 SET 400 SET – DEFINE HIGHER ANALOG FREQUENCY SETTING TO: 400 (default was 50.00)

PD144 SET 3600 SET – DEFINE RATED MOTOR REVOLUTION SETTING @60Hz TO: 3600 (default was 1440) or 3000 for 50Hz

PD008 SET 110 SET – DEFINE MAX VOLTAGE SETTING TO: 110V (default was 220)

Configuration for automatic control with 1F communication

PD001 SET 2 SET – DEFINE SOURCE OF OPERATING COMMANDS SETTING TO: SET BY COMMUNICATIONS PORTS AS COMMAND SOURCE (default was 0)

PD002 SET 2 SET – DEFINE SOURCE OF OPERATING FREQUENCY SETTING TO: SET BY COMMUNICATION PORTS. (default was 0)

PD163 SET 1 SET – DEFINE COMMUNICATION ADRESSES SETTTING TO: 1 - MUST MATCH ONEFINITY BUS-ID (default was 0)

PD164 SET 1 SET – DEFINE COMMUNICATION BAUD RATE SETTING TO: 9600 – MUST MATCH ONEIFINITY BAUD (default was 1)

PD165 SET 3 SET – DEFINE COMMUNICATION DATA METHOD SETTING TO: 8N1 for RTU – MUST MATCH ONEFINITY PARITY

Configuration to trigger SSR (i.e start pump and vacuum)

PD052 SET 2 SET – DEFINE Multi-Output 3(FA, FB, FC function)

PD053 SET 1 SET – DEFINE Multi-Output 4 (KA, KB function)

Lock VFD Config

PD000 SET 1 SET – Lock config