Hey Josh,

an emergency stop button shall not interrupt the power of a VFD. The only way to stop a spindle, including emergency stop, is to use the STOP mode of the VFD (either through front keypad, modbus command, or programmable input terminal with STOP function assigned to it). Some VFDs additionally have an emergency circuit support, like Omron MX2. See VFD manual. According to the updated IEC 60204-1, a VFD’s spindle STOP command is considered as a valid Safe Torque Off (STO) that fulfils the stop category 0 requirement (so allows to e.g. safely manually change the tool in this state).

No, but a ready-to-use cable is available, see link to GX-12 below.

For signal cable cross-section area, see VFD manual.

For GX-12 VFD control cable pinout and sources, see here:

If you use a VFD with single-phase AC input (which is the case if you have 110/220 V split-phase electricity), you need a 2+PE cable. If you use a VFD with single phase AC input on your VFD, the single-phase input current is about 2.5 x higher than the three-phase spindle output current, thus requiring a cable sufficient for such current. Remember a VFD is an AC-to-DC-to-three-phase-AC inverter. See input current specification of your VFD:

Images: Here you can see the nameplates of two 220 V VFDs for single-phase input for a 2.2 kW motor. As you can see, the max. input current is 24 A, which would require a 2+PE power supply cable of 6 mm² cross-section area (AWG 10), at least 4 mm² (AWG 12).

On the VFD input side, if you use 230 V from split-phase electricity, you only use the two hots. You need a 2+PE cable for this. The neutral is only necessary to grab a 115 V suplly if you need it.

On the VFD output side, there is no neutral, as there is no neutral on a spindle. The wires are U, V, W and PE, and shield. See here

An EMI filter is the most recommended accessory for a VFD. :warning: Be sure that the EMI filter is made for the VFD rated input current (here: 24 Ampères in the example above for a 220 V VFD for 2.2 kW spindle. An underdimensionated EMI filter is dangereous because the current constantly flows through its capacitors, so they have to be rated for that current.

Note that many cheap no-name / Huanyang spindles simply omit the VFD input current specification both on their nameplate and VFD manual. See Incorrect or missing data on cheap chinese VFDs and spindles for details.

If you have split-power electricity as is common in North America domestic areas, 230 V ist between two hots and 115 V is between one hot and neutral.

Usually you have a 24 V supply like Meanwell MDR10-24 or a MDR20-24
in your VFD control cabinet to drive the safety relay etc. (e.g. Omron G9SE). Using a separate power supply like this avoids concern about how the 24 V is connected to other things.